Determining amperage of a sub panel


Recommended Posts

Ignore the first response - The 20 amp subpanel is fed by a double-pole 240-volt breaker at the main service panel, and this single feed circuit is divided into additional branch circuits at the subpanel. If it is 20 amp, it probably is fed by 12 gauge wire. 30 amp is 10 gauge. Over 30 amps can cause 10 gauge wire to melt and become a fire hazard. If you want 40 amps in the garage, you need to replace the wire feeding the garage with 8 gauge wire.

The load on the subpanel could be anything. Add up the loads and that will give you more detailed info. In other words, say a 100W bulb draws .9A. And then you change out the 100W bulb for an LED which draws 1/12A. Now on that 20A circuit where you could have had 22 incandescent bulbs, you can now have 240 LED bulbs.

Edited by Bevo
Link to comment
Share on other sites

Currently, I have one 20 amp breaker in the sub panel. There are 4 outlets and one LED shop light on it.

I just want to add a second 20 amp breaker so that I can add 4 more outlets and two additional LED shop lights.

I guess I could could just run it all off the one breaker since I doubt it’d get to 20 amps total anyway. The highest load at once would be running a table saw, dust collector, 18v battery charging station, and lights at the same time.

Link to comment
Share on other sites

2 hours ago, CooterBrown said:

Currently, I have one 20 amp breaker in the sub panel. There are 4 outlets and one LED shop light on it.

I just want to add a second 20 amp breaker so that I can add 4 more outlets and two additional LED shop lights.

I guess I could could just run it all off the one breaker since I doubt it’d get to 20 amps total anyway. The highest load at once would be running a table saw, dust collector, 18v battery charging station, and lights at the same time.

Yeah, that would be the easiest. See how many amps the table saw and dust collector run. Typically, I think a table saw runs 6-16 Amps. Dust collectors run a lot also. https://www.woodmagazine.com/woodworking-tips/techniques/outfitting-woodworking-shop/critical-questions-about-workshop-wiring So, you could potentially have an issue.

If you have an issue with tripping the subpanel breaker, there is a decent chance that the builder put in wire larger than needed for that 20Amp breaker in the subpanel. I don't know electrical code, but I would think that if you have a 40Amp breaker at the main, code would require that the wire from the main to the subpanel would need to be able to handle the 40Amps.

Edited by Bevo
  • Like 1
Link to comment
Share on other sites

5 hours ago, CooterBrown said:

Went ahead and added a 20 amp circuit breaker. The table saw and dust collector are now on separate circuits. Each has 4 outlets and two shop lights. Easy Peasy. Thanks for the info.

Did you have a main switch to turn power off at sub panel to install?   Or did you  have to turn off main switch at main panel to make sure no electricity running to sub panel? 

Link to comment
Share on other sites

10 hours ago, Hornbeliever said:

Did you have a main switch to turn power off at sub panel to install?   Or did you  have to turn off main switch at main panel to make sure no electricity running to sub panel? 

It isn't hard, but you have to know what you are doing. He had a 40Amp breaker at the main. After flipping the breaker, he could see if it turned off power to the subpanel. Once he knew he was good, it is a pretty straight forward project. He could inspect the wires to make sure they could handle the current and then install the breaker and move some wires and install a few more wires for the power tools and new outlets.

  • Hook 'Em 1
Link to comment
Share on other sites

Just now, Bevo said:

It isn't hard, but you have to know what you are doing. He had a 40Amp breaker at the main. After flipping the breaker, he could see if it turned off power to the subpanel. Once he knew he was good, it is a pretty straight forward project. He could inspect the wires to make sure they could handle the current and then install the breaker and move some wires and install a few more wires for the power tools and new outlets. Since it is in the garage, a GFCI circuit is necessary, though.

 

Link to comment
Share on other sites

22 hours ago, CooterBrown said:

Went ahead and added a 20 amp circuit breaker. The table saw and dust collector are now on separate circuits. Each has 4 outlets and two shop lights. Easy Peasy. Thanks for the info.

What size wire did you use to feed the new outlets? 

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.



×
×
  • Create New...